Hi,
Hello Refsam,
As long as the two machines (Client and Server) are on the same Domain and can ping each other you should just be able to configure DCOM per the following guide to get them communicating:
BRgds,
KC
thank you for your answer.
I have configured DCOM, but there is still a problem where the server tag can be imported into kepware but on the quick client, all values are "unknown".
a notification like this appears.
I've followed the way to solve this problem on PTC kepware, but it still doesn't work
Hello Refsam,
It sounds like we will need to dig into this. Please open a support ticket at the following link:
https://www.ptc.com/en/support/kw-case-logger?&msg=1
Thanks,
KC
Can u provide an update? I'm having the same issue. I'm able for Kepware to import the Wincc OPCDA server tags, but the kepware OPC DA Client is unable to read the values. OPC Quick Clint is able to read the Wincc OPC DA server with no issues.
Matt
Previously the problem was because the user did not have access,
to solve it, I created the same user and pass on each device and added them to the group Administrators, and followed the DCOM settings again